  • erro h1 no display do gree de 12000 BTU

    o meu ar condicionado gree de 12000BTU no quente apresenta um erro o h1 no display e não liga a evaporadora, oq significa este erro??

  • #2
    Error code = F1
    error = Indoor coil temperature failure

    Error code = F2
    error = outdoor ambient temperature failure

    Error code = F3
    error = outdoor coil temperature failure

    GREE Split air conditioners Error Code

    Name of malfunction = Refrigerant system high pressure protection
    Display of double eight code = E1
    Display of lamp
    Running lamp = blink 1 time
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Anti-freezing protection
    Display of double eight code = E2
    Display of lamp
    Running lamp = blink 2 times
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Compressor exhaust high temperature protection
    Display of double eight code = E4
    Display of lamp
    Running lamp = blink 4 times
    Cooling lamp =
    Heating lamp =

    Name of malfunction = AC over-current protection
    Display of double eight code = E5
    Display of lamp
    Running lamp = blink 5 times
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Communication failure between indoor unit and outdoor unit
    Display of double eight code = E6
    Display of lamp
    Running lamp = blink 6 times
    Cooling lamp =
    Heating lamp =

    Name of malfunction =Anti-high temperature protection
    Display of double eight code = E8
    Display of lamp
    Running lamp = blink 8 times
    Cooling lamp =
    Heating lamp =

    Name of malfunction = No feedback of indoor fan motor
    Display of double eight code = H6
    Display of lamp
    Running lamp = blink 11 times
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Jumper cap malfunction protection
    Display of double eight code = C5
    Display of lamp
    Running lamp = blink 15 times
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Indoor ambient sensor open or short circuit
    Display of double eight code = F1
    Display of lamp
    Running lamp =
    Cooling lamp = blink 1 times
    Heating lamp =

    Name of malfunction = Indoor tube sensor open or short circuit
    Display of double eight code = F2
    Display of lamp
    Running lamp =
    Cooling lamp = blink 2 times
    Heating lamp =

    Name of malfunction = Outdoor ambient sensor open or short circuit
    Display of double eight code = F3
    Display of lamp
    Running lamp =
    Cooling lamp = blink 3 times
    Heating lamp =

    Name of malfunction = Outdoor tube sensor open or short circuit
    Display of double eight code = F4
    Display of lamp
    Running lamp =
    Cooling lamp = blink 4 times
    Heating lamp =

    Name of malfunction = Exhaust sensor open or short circuit
    Display of double eight code = F5
    Display of lamp
    Running lamp =
    Cooling lamp = blink 5 times
    Heating lamp =

    Name of malfunction = Over load limit/drop frequency
    Display of double eight code = F6
    Display of lamp
    Running lamp =
    Cooling lamp = Blink 6 times
    Heating lamp =

    Name of malfunction = Over current limit/drop frequency
    Display of double eight code = F8
    Display of lamp
    Running lamp =
    Cooling lamp = blink 8 times
    Heating lamp =

    Name of malfunction = High exhaust temperature limit/drop frequency
    Display of double eight code = F9
    Display of lamp
    Running lamp =
    Cooling lamp = blink 9 times
    Heating lamp =

    Name of malfunction = Over voltage protection for PN
    Display of double eight code = PH
    Display of lamp
    Running lamp =
    Cooling lamp = blink 11 times
    Heating lamp =

    Name of malfunction = AC current detect circuit malfunction
    Display of double eight code = U5
    Display of lamp
    Running lamp =
    Cooling lamp = blink 13 times
    Heating lamp =

    Name of malfunction = Compressor reverse protection
    Display of double eight code = U4
    Display of lamp
    Running lamp =
    Cooling lamp = blink 14 times
    Heating lamp =

    Name of malfunction = Over compressor phase current protection
    Display of double eight code = P5
    Display of lamp
    Running lamp =
    Cooling lamp = blink 15 times
    Heating lamp =

    Name of malfunction = Inlet tube sensor malfucntion
    Display of double eight code = b5
    Display of lamp
    Running lamp =
    Cooling lamp = blink 19 times
    Heating lamp =

    Name of malfunction = Outdoor DC fan motor malfunction
    Display of double eight code = L3
    Display of lamp
    Running lamp =
    Cooling lamp = blink 21 times
    Heating lamp =

    Name of malfunction = Outlet tube sensor malfunction
    Display of double eight code = b7
    Display of lamp
    Running lamp =
    Cooling lamp = blink 22 times
    Heating lamp =

    Name of malfunction = Compressor overload sensor malfunction
    Display of double eight code = FE
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Defrosting
    Display of double eight code = H1
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 1 time

    Name of malfunction = Static clearing dust protection
    Display of double eight code = H2
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 2 times

    Name of malfunction = Compressor overload protection
    Display of double eight code = H3
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 3 times

    Name of malfunction = System abnormal protection
    Display of double eight code = H4
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 4 times

    Name of malfunction = IPM protection
    Display of double eight code = H5
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 5 times

    Name of malfunction = PFC protection
    Display of double eight code = HC
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 6 times

    Name of malfunction = Compressor loss step protection
    Display of double eight code = H7
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 7 times

    Name of malfunction = Heating anti-high temperature drop frequency
    Display of double eight code = HO
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 10 times

    Name of malfunction = Start-up failure
    Display of double eight code = Lc
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 11 times

    Name of malfunction = Compressor protection against loss of phase
    Display of double eight code = U2
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 12 times

    Name of malfunction = Compressor phase current detection circuit malfunction
    Display of double eight code = U1
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 13 times

    Name of malfunction = Compressor demagnetization protection
    Display of double eight code = HE
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 14 times

    Name of malfunction = Loading EEPROM malfunction
    Display of double eight code = EE
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 15 times

    Name of malfunction = Communication failure between main board and driver board
    Display of double eight code = P6
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 16 times

    Name of malfunction = Capasitor charge malfunction
    Display of double eight code = PU
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 17 times

    Name of malfunction = IPM sensor circuit malfunction
    Display of double eight code = P7
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 18 times

    Name of malfunction = IPM high temperature protection
    Display of double eight code = P8
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 19 times

    Name of malfunction = PN voltage drop protection
    Display of double eight code = U3
    Display of lamp
    Running lamp =
    Cooling lamp = blink 20 times
    Heating lamp =

    Name of malfunction = Low PN voltage protection
    Display of double eight code = PL
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = blink 21 times

    Name of malfunction = Current detect circuit malfunction or current sensor malfunction
    Display of double eight code = Pc
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Compressor loss of phase protection
    Display of double eight code = Ld
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Compressor or locked rotary protection
    Display of double eight code = LE
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = IPM over temperature limit/drop frequency
    Display of double eight code = EU
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = 4-way valve reversal abnormal
    Display of double eight code = U7
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Disconnection of the exhaust temperature sensor
    Display of double eight code = U8
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = AC power zero voltage detect error
    Display of double eight code = U9
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Over tube temperature drop frequency
    Display of double eight code = FA
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp =

    Name of malfunction = Anti-freezing limit/drop frequency
    Display of double eight code = FH
    Display of lamp
    Running lamp =
    Cooling lamp =
    Heating lamp = - See more at: http://errorcodeairconditioning.blog....EFotuKmF.dpuf

    Comment


    • #3
      pressostato de alta pressão, unidade externa - OVC